Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Special confinement for columns in AS3600

Status
Not open for further replies.

asixth

Structural
Joined
Feb 27, 2008
Messages
1,333
Location
GB
I don't like the all or nothing approach of the special confinement requirements in AS3600.

I agree with the no special requirements under fc=50MPa and a confinement of 0.1*fc above 0.75*phi*Nuo. But I think it should have an intermediate confinement requirement between these two values of 5MPa. Please see the attached diagram.
 
 http://files.engineering.com/getfile.aspx?folder=11a3ed8a-e6d3-415e-b432-d9f5901e03b6&file=Confinment_Diagram.pdf
Asixth,

You still need confinement in those areas based on the general confinement rules in clause 10.7.4 and table 10.7.4.3. It is just not based on a strength calculation as is required for the Special Confinement zones in Fig 10.7.3.1(A).
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top