@Enable Excellent info you provided. Thank you for sharing. Yet, the above two statements confused me. Do you generally shore concrete elements before repairing or not?
I probably could have been clearer with those statements. But
@BridgeSmith has is right. Passive Shoring and Active Shoring are the technical terms sometimes used to distinguish shoring that is merely placed to handle any loads that redistribute during the repair (Passive Shoring) and shoring that unloads the member prior to the repair (Active Shoring). Below is a rough, rough guide to when each is typically utilized.
No Shoring: Minor repairs that do not extend beyond the cover. These are cosmetic in nature and don’t go into the core of the element being repaired. You would patch these with SikaTop 123 or similar.
Passive Shoring: Flexural members (e.g. beams, slabs, foundation walls, etc) or very lightly loaded axial members (e.g. garage columns) where a modest increase in deflection post-repair is not a huge issue. Usually the repair extends into the core of the member and at least past the primary steel. This constitutes the bulk of shoring used on repairs in my experience.
Active Shoring: Axially loaded members that have a fair amount of load on them (e.g. building columns) where very sudden movements during / after repairs would be a big deal. The active nature of it also doubles as a load test of the shoring assembly, so even if movement is not a concern, it is the system of choice for axially loaded building elements.
Here are two projects that should get the idea across (for Passive vs Active).
Project 1 (Passive): Single story parking garage with base column repair. We used passive shoring here simply distributing over a large enough area that movements would be tolerable during load redistribution.
Project 2 (Active): Building column holding up an 18-story occupied building (~ 1million pounds factored) that needs to be demolished and replaced. Active shoring with hydraulic jacks used to transfer the load to the shoring prior to demolition. For obvious reasons we want to test the system before it is relied upon for safety of the structure! We’re actually just completing this guy and you can follow along online where we push the data to an online dash board we made (we should start jacking tomorrow and continue over a 3 day period):
https://www.enable-inc.com/live-feed