Spacing between conduits

Status
Not open for further replies.

timm333

Electrical
Jun 4, 2009
121
Can power and instrument conduits run side by side? If not then what should be the minimum distance between them…
 
Replies continue below

Recommended for you

Define "power".

Also, are you asking about code requirements? If so, which code?

Or are you concerned about noise and other EMC issues?

Our mind readers are out today.

David Castor
 
There are two power conduits. One for 120/208V 250A cable, and the other is for 480V 30A cable. The power loads are lighting, HVAC, door opener etc.

By instrument coduits I mean the conduits for paging speakers and video cameras.

How much should the distance be between power and instrument conduits?
 
If you are running in steel conduit and using shielded cable, you shouldn't have a problem. If the 250 A circuit is in PVC conduit, I'd try to maintain 12 inch separation. The 30A circuit shouldn't be a problem.

David Castor
 