Hello,
A house heating load as following (the numbers are only as example):
- Winter outside/inside temperature design : 0F/70F
- Supply air temperature: 120F
- space load (envelop + infiltration): 60000 Btu/hr
- OA ventilation requirement 100 cfm, (7560 Btu/hr)
the question is about air flow calculation:
1- cfm = 60000/(1.08*(120-70)) = 1111.11 cfm
2- cfm = 67560/(1.08*(120-70)) = 1251.11 cfm
which one is much correct.?