The building was built in 1960's and we did not find any drawings for this building. It is a one story building about 20' tall, 84' wide and 165' long.
The roof includes ballasted roof (ply felt and gravel, fiber board and rigid insulations), metal deck and open bar web joists (span is about 33’).
The end CMU walls (84’ long) are load bearing walls supporting the joists. The side CMU walls are not load bearing and are not reinforced except the bond beam at the top of the wall. I have some questions when I check the buildings.
1. Should I use Component and Cladding wind loads to check the CMU walls?
2. The side CMU wall (165’ long) has a 12” thick strip footing, which is 3’-6” below grades. So should I use 20’+3’-6”-12” =22’-6” to check the wall? The wall is not connected to the interior slab-on-grade. Can I use the passive soil pressure as a support and use a span of 20’ to check the wall?
3. The roof joists are supported by some continuous small W shape beam. So there are negative moments near the columns. If the length of negative moment area is longer than Lp , then the nominal moment capacity of the beam is less than Fy*Zx. Is that true?
4. There is section modulus Sx and plastic section modulus Zx for each W beam. I understand the Sx*Fy is the moment causing the extreme fiber to yield. So for Zx*Fy, the total flange will yield or total W section yields? Any reference I can study? (some parts of steel beam has been repaired with steel plates at the flanges of W beam, so I have to find the Zx of repaired sections)
5. The geotechnical engineer checked the soil bearing capcities. For 4000 psf, the estimated settlement is 1” and for 3000 psf , ½” with the expected column loads (we are going to build a roof above the existing roof). So which one should I use? Or the PE who is going to sign the drawing will have the final say.
Thanks
The roof includes ballasted roof (ply felt and gravel, fiber board and rigid insulations), metal deck and open bar web joists (span is about 33’).
The end CMU walls (84’ long) are load bearing walls supporting the joists. The side CMU walls are not load bearing and are not reinforced except the bond beam at the top of the wall. I have some questions when I check the buildings.
1. Should I use Component and Cladding wind loads to check the CMU walls?
2. The side CMU wall (165’ long) has a 12” thick strip footing, which is 3’-6” below grades. So should I use 20’+3’-6”-12” =22’-6” to check the wall? The wall is not connected to the interior slab-on-grade. Can I use the passive soil pressure as a support and use a span of 20’ to check the wall?
3. The roof joists are supported by some continuous small W shape beam. So there are negative moments near the columns. If the length of negative moment area is longer than Lp , then the nominal moment capacity of the beam is less than Fy*Zx. Is that true?
4. There is section modulus Sx and plastic section modulus Zx for each W beam. I understand the Sx*Fy is the moment causing the extreme fiber to yield. So for Zx*Fy, the total flange will yield or total W section yields? Any reference I can study? (some parts of steel beam has been repaired with steel plates at the flanges of W beam, so I have to find the Zx of repaired sections)
5. The geotechnical engineer checked the soil bearing capcities. For 4000 psf, the estimated settlement is 1” and for 3000 psf , ½” with the expected column loads (we are going to build a roof above the existing roof). So which one should I use? Or the PE who is going to sign the drawing will have the final say.