Sep 12, 2007 #1 TenPenny Mechanical Joined Nov 7, 2006 Messages 1,143 Location CA Anyone here familiar with any NFPA rules that would apply to solvent (toluene) tanks in a haz waste collection facility? I'm starting the very basics of research on this, any genuine help would be appreciated.
Anyone here familiar with any NFPA rules that would apply to solvent (toluene) tanks in a haz waste collection facility? I'm starting the very basics of research on this, any genuine help would be appreciated.
Sep 12, 2007 #2 stookeyfpe Specifier/Regulator Joined Mar 13, 2005 Messages 1,882 Location US The tank volume would be a good start. Do you own a copy of NFPA 30? If not, order it now. Are you looking for guidance or free consulting? Upvote 0 Downvote
The tank volume would be a good start. Do you own a copy of NFPA 30? If not, order it now. Are you looking for guidance or free consulting?
Sep 13, 2007 Thread starter #3 TenPenny Mechanical Joined Nov 7, 2006 Messages 1,143 Location CA Guidance only. Tank vol is 300-600 gal. If NFPA 30 is the place to start, then that's where I'll start. That's the sort of info that I'm looking for, not free consulting. Upvote 0 Downvote
Guidance only. Tank vol is 300-600 gal. If NFPA 30 is the place to start, then that's where I'll start. That's the sort of info that I'm looking for, not free consulting.
Sep 13, 2007 #4 cdafd Specifier/Regulator Joined Aug 18, 2005 Messages 2,953 Location US are they trying to do any transfer of liquid inside the building??? Upvote 0 Downvote
Sep 13, 2007 Thread starter #5 TenPenny Mechanical Joined Nov 7, 2006 Messages 1,143 Location CA Yes, it's a collection/transfer facility for used hazardous wastes, and at the moment, the tanks are polypropylene. Upvote 0 Downvote
Yes, it's a collection/transfer facility for used hazardous wastes, and at the moment, the tanks are polypropylene.
Oct 11, 2007 #6 MJCronin Mechanical Joined Apr 9, 2001 Messages 5,102 Location US Ten.... UUUUUmmmmmmm... Collecting flammable liquids in poly (or any other type of plastic tanks is not a good idea and may be banned by NFPA-30 My recollection only -MJC Upvote 0 Downvote
Ten.... UUUUUmmmmmmm... Collecting flammable liquids in poly (or any other type of plastic tanks is not a good idea and may be banned by NFPA-30 My recollection only -MJC
Oct 12, 2007 #7 psafety Specifier/Regulator Joined Mar 27, 2001 Messages 229 Location US Yes, banned. There is even a minimum melt temperature for valves and valve internals. Upvote 0 Downvote
Oct 19, 2007 #8 MJCronin Mechanical Joined Apr 9, 2001 Messages 5,102 Location US Ten.... Steel, steel, steel....... Read page # 6 and Section 3.3.2 of this report: http://www.csb.gov/completed_investigations/docs/CSBBethuneFinalReport.pdf Take a good look at Figures 5 & 6.... the backhoe operator died Also review OSHA 1910.106 on use of plastic materials in fire exposure situations. Let us know about your final decision on materials usage -MJC Upvote 0 Downvote
Ten.... Steel, steel, steel....... Read page # 6 and Section 3.3.2 of this report: http://www.csb.gov/completed_investigations/docs/CSBBethuneFinalReport.pdf Take a good look at Figures 5 & 6.... the backhoe operator died Also review OSHA 1910.106 on use of plastic materials in fire exposure situations. Let us know about your final decision on materials usage -MJC