In my experience, mostly with low HP and long lead lengths, solid core is a no-no. HF cable charging currents are always higher on solid; the higher currents are due to the "skin effect" or the fact that your dealing purely with surface current. The surface current is directly underneath your insulation, so your capacitance values go up considerably over the length of the cable, just because of the HF component of the VFD.
Even though most people will recommend a shielded VFD cable for any drive motor combination, it should be noted that shielded is the worst performer for cable charging and common mode currents. The only true benefit of shielded is RF immunity for nearby equipment, and the reduction of ground circulating current in the VFD motor system. The shield, when terminated on both sides provides a low impedance return for the HF vs. the basic bond lead.
It has been my experience simply from a VFD and motor performance perspective, that the best performer is good ol' 600V stranded in conduit. The lack of symmetry in the run keeps capacitive effects low, and if the conduit is up to snuff, your RF mitigation will be minimal.
The secondary concern for solid core is at the motor termination end; solid core has a tendency to suffer insulation scraps at the entry point and in your bends. While your average 460V RMS won't find this pin-hole, the VFD's HF Switched DC output... will. At longer lead lengths, this becomes a greater concern, as the impedance mismatch in the cable will sometimes produce twice buss at the motor terminals (reflected wave). For a 460V drive, this is approaching the 1400Vp mark. Insulation pin-hole "found".