Jul 16, 2003 #1 lotus7312 Chemical Joined May 29, 2003 Messages 24 Location US Dear all, I have a solenoid valve with 220V/50Hz. Can I use a controller with on-off control relay to operate this solenoid valve? Thank you
Dear all, I have a solenoid valve with 220V/50Hz. Can I use a controller with on-off control relay to operate this solenoid valve? Thank you
Jul 16, 2003 #2 jbartos Electrical Joined Jan 15, 2000 Messages 6,440 Suggestion: Yes. Check with the solenoid manufacturer how often or how many ON/OFFs per time interval, maximum, are permitted not to burn it. Upvote 0 Downvote
Suggestion: Yes. Check with the solenoid manufacturer how often or how many ON/OFFs per time interval, maximum, are permitted not to burn it.
Jul 19, 2003 #3 mdonner Electrical Joined Mar 2, 2003 Messages 61 Location IL Tip Check solenoid current and power factor agains controller data sheet corresponding values. If exceeded, use properly sized buffer relay. Upvote 0 Downvote
Tip Check solenoid current and power factor agains controller data sheet corresponding values. If exceeded, use properly sized buffer relay.