ASCE 7.05 in commentary C7.4 seems to concurr.
This may result in the elimination of snow loads on upper portions of the roof and their concentration on lower portions.
Also, what the
California Department of General Services . Division of the State Architect . Interpretation of Regulations Document
DSA (SS) IR 16-8 Solar Photovoltaic and Thermal
(iss 08-15-08) Systems Acceptance Requirements Page 1 of 5
SOLAR PHOTOVOLTAIC AND THERMAL
SYSTEMS ACCEPTANCE REQUIREMENTS
References: 2007 California Building Code (CBC), Sections 1609A and 1613A Issued 08-15-08
IR 16-8
has to say is
6.1.5 Roof Live Loads on Panels. It is not necessary to include roof live load (20 psf) in the area(s) covered by the panels when these area(s) are inaccessible, or
fenced off with posted signs prohibiting storage under the panels.
When applicable, include snow loads and loads from snow drift.
It interestingly resolves -their way- the question on if keeping the live load on the solar panels plan.
For Wisconsin...
"The UDC does not set lower snow live load values for roofs with glass or other slippery surfaces unless per s. Comm 21.27(1)(b), the slope is 7 in 12 or greater just as for other roof types. Otherwise, attached greenhouses, solar spaces, solar panels and other similar roof construction should be designed to withstand 40 or 30 PSF for zone 1 or 2 respectively."