While 2000 PSF is common for very loose conditions, it may be a little much, depending. I'd go back and provide typical service column loads and ask for an estimate of settlement at that 2,000 PSF. What is interesting is the water levels at end of boring show "none". Many times below the water table, blow counts drop a lot as compared to above the water table. "Wet" samples may mean that, but why no readings later? Maybe jetting the interior was source of water in the samples. I also look at this and wonder if this is natural or a filled site. In some conditions the method of advancing the boring can result in low blow counts. Jetting out the interior of hollow stem augers before driving the spoon easily can cause the conditions noted, but don't correctly show the soil density. Once cleaned out to bottom of augers, continuing the jet can greatly disturb what then is sampled. Specifically you need to know if a jet was used or if an interior plug is routinely used inside the augers to prevent filling the auger with soil. I'd want to stand and watch the guys before I make a judgement on that however. In summary there are some questions that need answering. This also is in the realm of dealing with responsibility for performance, etc. Changing design numbers from the report may change the degree of responsibility that comes from the geotech.