Hi,

I have read thread256-285800 and got stuck here:
"If you look at Bowles Table 9-1, modulus subgrade, kv (kN/m3)
approx equal to 240 Cu (kPa).
Allowable bearing pressure, qa (kPa) = Nc Cu / SF = (5.14 /3) Cu..."

Bowles Table 9-1 shows ks (not kv), and there is no Cu there...
Also, where is the 5.14 value coming from?

Thanks.

 
Replies continue below

Recommended for you

Nc is bearing capacity factor of 5.14. This is for phi = 0
 
Thanks, EireChch - where could I find a reference for this?

So for phi=0 (cohesive soils) use Nc=5.14, but what if c=0 or for c-phi soil types?

 
Any soil mechanics/ foundation book (bowles) that has a section on bearing capacity shows Nc values for phi = 0 to phi = 40+. Its a row of tables.

c is typically taken as 0 in c-phi soils as it is conservative (generally).

When c = 0 the first part of the bearing capacity equation is ignored. The second and third parts, which includes Ngamma and Nq are used to calculate bearing capacity.
 