I've got a project that's essentially a big two story house. It has a first level slab-on-grade.
I called for a 4000 psi cast-in-place slab-on-grade. I called for 4000 psi concrete as I know that 4000 psi concrete requires less water, and ultimately gives a better end product with less shrinkage cracking and a more durable surface.
When my test reports came back, at 7 days, I was only getting 1,000 psi breaks on my cylinders. We rebound tested the slab to find the areas of relative weak concrete, then cored the slab and tested the cores in accordance with ACI. Tests came back at 14 days as being 1,100, 1,200, and 1,250 psi concrete.
Structurally, I don't believe there's a problem, as the stud bearing walls do bear on the slab, but, I have placed a CMU foundation wall below all bearing walls that ultimately bears on a continuous 24" wide x 12" thick concrete footing. The only thing the slab has to do is transfer the vertical force directly thru from the wall above to the CMU below....and I know the concrete will not be crushed.
But what about serviceability? I'm sure we're more likely to see shrinkage cracking...but what about hazing/crazing of the concrete. What effect may this have on finishes?
FYI, I did require a high quality vapor barrier beneath the slab as well as 4" granular (#57 stone) fill.
Does anyone see a potential problem with the low compressive strength concrete I'm overlooking?
Thanks in advance for your opinion!!
I called for a 4000 psi cast-in-place slab-on-grade. I called for 4000 psi concrete as I know that 4000 psi concrete requires less water, and ultimately gives a better end product with less shrinkage cracking and a more durable surface.
When my test reports came back, at 7 days, I was only getting 1,000 psi breaks on my cylinders. We rebound tested the slab to find the areas of relative weak concrete, then cored the slab and tested the cores in accordance with ACI. Tests came back at 14 days as being 1,100, 1,200, and 1,250 psi concrete.
Structurally, I don't believe there's a problem, as the stud bearing walls do bear on the slab, but, I have placed a CMU foundation wall below all bearing walls that ultimately bears on a continuous 24" wide x 12" thick concrete footing. The only thing the slab has to do is transfer the vertical force directly thru from the wall above to the CMU below....and I know the concrete will not be crushed.
But what about serviceability? I'm sure we're more likely to see shrinkage cracking...but what about hazing/crazing of the concrete. What effect may this have on finishes?
FYI, I did require a high quality vapor barrier beneath the slab as well as 4" granular (#57 stone) fill.
Does anyone see a potential problem with the low compressive strength concrete I'm overlooking?