- Feb 8, 2004
- 51
This question involves ongoing practices with respect to supplying snuffing steam to sulfur storage tanks. According to NFPA 655 (2001), if used, snuffing steam should be provided at a rate of 8 lb/min per 100 ft³ of EMPTY tank volume. For a tank measuring 30 ft OD x 16 ft high, that amounts to something on the order of ~54,000 lb/hr, which in turn mandates a 12" line for 50 psig steam. That's pretty big.
What I would like to know is what others have encountered in terms of snuffing steam line size for a given tank size.
Thanks.
What I would like to know is what others have encountered in terms of snuffing steam line size for a given tank size.
Thanks.