ROCHESTER
Mechanical
- Nov 2, 2002
- 33
I have the following system:
[ol]
[li]BL-1, BioPharm, cell culture production.[/li]
[li]50,000 S.F. suite of clean rooms[/li]
[li]Two ~ 40,000 CFM AHUs; 100% outside air[/li]
[li]100% exhaust with no heat/cooling recovery
[/ol]
The New England facility was commissioned last fall. Under certain powdery snow conditions, and we had snow drawn into the intake and foul the pre-filters. The engineering firm hired to fix this is proposing a "snow eliminator"
The price estimate came in a > $100,000. Questions:
[ol]
[li]Does a BL-1 facility REQUIRE 100% outside air design?[/li]
[li]Is a desiccant wheel usable with a BL-1 AHU[/li]
[li]If a desiccant wheel can't be used, wouldn't an air-to-air heat exchanger provide the same function as the snow eliminator and save energy at the same time?[/li]
[li]What's a ball-park capital cost for a 40,000 CFM air-to-air heat exchanger unit?[/li]
[/ol]
[ol]
[li]BL-1, BioPharm, cell culture production.[/li]
[li]50,000 S.F. suite of clean rooms[/li]
[li]Two ~ 40,000 CFM AHUs; 100% outside air[/li]
[li]100% exhaust with no heat/cooling recovery
[/ol]
The New England facility was commissioned last fall. Under certain powdery snow conditions, and we had snow drawn into the intake and foul the pre-filters. The engineering firm hired to fix this is proposing a "snow eliminator"
The price estimate came in a > $100,000. Questions:
[ol]
[li]Does a BL-1 facility REQUIRE 100% outside air design?[/li]
[li]Is a desiccant wheel usable with a BL-1 AHU[/li]
[li]If a desiccant wheel can't be used, wouldn't an air-to-air heat exchanger provide the same function as the snow eliminator and save energy at the same time?[/li]
[li]What's a ball-park capital cost for a 40,000 CFM air-to-air heat exchanger unit?[/li]
[/ol]