David said:
CNE is on the utility side of the meter
Both the primary and secondaries are grounded at each transformer.
This has to a lot to do with lightning protection on the primary.
In the case of one ground being lost, there are backup grounds.
Utility grounds are outside, may be poorly protected and may go for decades without inspection and/or maintenance.
David said:
SNE is everywhere beyond the meter. Probably no options in either case.
Words:
Beyond the meter there may be, and often are, several grounds.
You may mean to say, SNEC Single Neutral to Earth Connection.
You may have many interconnected grounds past the meter, but only one CONNECTION to the system neutral.
System ground connecting links are generally well protected from mechanical damage and the environment.
More than one ground CONNECTION to the system neutral may defeat ground fault detection and protection or make it more difficult.
More than one ground CONNECTION to the system neutral is prohibited by codes in North America.
There are few exceptions.
In the unlikely event of the loss of the neutral-ground connection, the utility multiple grounds will provide back-up.