not seeing an exception, except maybe have to test to manufacture testing procedures
14.4.4.3.4 To ensure that each smoke detector is within its listed and marked sensitivity range, it shall be tested using any of the following methods:
(1)
Calibrated test method
(2)
Manufacturer’s calibrated sensitivity test instrument
(3)
Listed control equipment arranged for the purpose
(4)
Smoke detector/fire alarm control unit arrangement whereby the detector causes a signal at the fire alarm control unit where its sensitivity is outside its listed sensitivity range
(5)
Other calibrated sensitivity test methods approved by the authority having jurisdiction