Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Small Elevator Structural Design Considerations [Lateral]

Status
Not open for further replies.

RareBugTX

Structural
Joined
Aug 31, 2004
Messages
214
Location
US
Hello All:

Looking for your feedback on structural considerations for a small 2000 lb elevator in an existing 2 story building. I know there is a lot to it. Building is heavy timber and wood floor joists, so no major troubles making the floor holes. Elevator is hoist type and I would almost call it residential. No seismic involved for lateral forces against the building frame.
The only thing I could think of is footings for DL + LL.I was wondering what you have used for vibration or the like on the frame.(or any other lateral).

Thanks a lot.

RarebugRA
 
As far as dynamic loading, you can do one of three things, as I see it:

1. Contact the rep from the manufacturer who is handling the elevator, and ask for them to provide an equivalent static loading from the maximum expected dynamic conditions.
2. Obtain the cut sheets on the elevator. It should have the dynamic operating criteria. Calculate the equivalent static loading using some general physics equations.
3. Assume some very conservative additional % of self-weight to impart an equivalent static load.

They (the manufacturer) sold the elevator, so they *shouldn't* have trouble giving you what you need. However, if the resist for some reason, you should absolutely have access to the cut sheets. The last one should only be used in non-critical situations.

In Russia building design you!
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top