Slide valve potentiometer

Status
Not open for further replies.

helpyou

Automotive
Sep 26, 2011
79
HI

There is a compressor slide valve. feedback is potentiometer connected to a 4-20mA transmitter. Existing potentiometer resistance is 1 Kohm. My question is, If I replace 1 KOHM potentiometer with a 10 Kohm, will the circuit work and still get feedback or I have to make other adjustments ?

Other than resistance, any other thing I should look at when selecting an alternative potentiometer?

Thank you .
 
Replies continue below

Recommended for you

Both. Your original pot is 1K, which is 10% of the range of the 10K pot. That means the whatever is reading the output will think the valve is closed, when it's barely 10% of the way there.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! faq731-376 forum1529 Entire Forum list
 