In SKM manual, when running multiple on-site generators that are connected away from the utility:
"An on-site generator that operates in parallel with the utility source may be defined as either a PV- or PQ-type generator..The swing bus generator or utility source must supply any deficiency in generation, and all losses. If there is excess generation in the system, the source bus acts to absorb the excess generation.Usually, a system requires only a single swing bus. Multiple swing buses may be used to model large systems having multiple connections to a utility. Therefore, the exact utility voltages and angles may be specified. Additionally, multiple independent systems require that you specify a swing bus for each system. Only one swing bus may be specified at a single bus". Co-generation modeled as PV-type generators which are not located near the utility or swing bus generator will serve to regulate the voltage at the generator bus. PTW attempts to hold the bus voltage at the target level within the reactive power range. It may not be possible to obtain the target voltage. PTW will maintain the kW output of the generator and allow the voltage to float to the reactive power limit".
I am a bit confused with the part that says: "PTW attempts to hold the bus voltage at the target level within the reactive power range. It may not be possible to obtain the target voltage. PTW will maintain the kW output of the generator and allow the voltage to float to the reactive power limit"
What does this mean?
I have a little bit of dilemna on the load flow because, if the in-plant generation exceeds the load by a couple og MWs, the power flow is back-feeding to the transformers. In reality, we intend to maximize and adjust the on-site generation in such a manner that i will limit my electric utility costs and during an operation where the utility and generation are on-line, I optimize my generators to limit my utility consumption. Is there a way I can do that in a load flow study where the calculation is static and not dynamic.
"An on-site generator that operates in parallel with the utility source may be defined as either a PV- or PQ-type generator..The swing bus generator or utility source must supply any deficiency in generation, and all losses. If there is excess generation in the system, the source bus acts to absorb the excess generation.Usually, a system requires only a single swing bus. Multiple swing buses may be used to model large systems having multiple connections to a utility. Therefore, the exact utility voltages and angles may be specified. Additionally, multiple independent systems require that you specify a swing bus for each system. Only one swing bus may be specified at a single bus". Co-generation modeled as PV-type generators which are not located near the utility or swing bus generator will serve to regulate the voltage at the generator bus. PTW attempts to hold the bus voltage at the target level within the reactive power range. It may not be possible to obtain the target voltage. PTW will maintain the kW output of the generator and allow the voltage to float to the reactive power limit".
I am a bit confused with the part that says: "PTW attempts to hold the bus voltage at the target level within the reactive power range. It may not be possible to obtain the target voltage. PTW will maintain the kW output of the generator and allow the voltage to float to the reactive power limit"
What does this mean?
I have a little bit of dilemna on the load flow because, if the in-plant generation exceeds the load by a couple og MWs, the power flow is back-feeding to the transformers. In reality, we intend to maximize and adjust the on-site generation in such a manner that i will limit my electric utility costs and during an operation where the utility and generation are on-line, I optimize my generators to limit my utility consumption. Is there a way I can do that in a load flow study where the calculation is static and not dynamic.