Sizing Temporary Protective Grounds

Status
Not open for further replies.

BrkfldEE

Electrical
Sep 22, 2009
25
thread238-82004
Does anyone have a clear method to size temporary protective grounds? I have read IEEE 1246 and that doesn't seem to go into enough detail. I have read IEEE 1048 and it references some tables in ASTM F855-1997. However I can only get access to ASTM F855-2009 which doesn't seem to have the tables anymore. ASTM F855-2009 has Table 1 for X/R ratios of 1.8 or less and Table 2 for X/R ratios of greater than 1.8 however I can't understand how to use table 2, it doesn't seem to give enough information. Any help or guidance would be appreciated.
 
Replies continue below

Recommended for you

Check out Chance Section 3000 (Grounding Equipment) . We size our grounds for the breaker failure clearing time. A few locations require 2 sets of grounds due to high fault current or slow clearing times, which is clearly posted with signs at the grounding locations. The portable grounds should be a short as possible.
 