deetz
Electrical
- Nov 19, 2010
- 89
So when sizing the primary wires for a transformer that's powering a machine, can you use the machine loads for the sizing of the wires for the primary? That is after you do your calculations. Say you have a 70kva load machine that is supplied by a 75kva transformer. Can you take 70kva times the 831.36 to get your amps for wire sizing? The machine is 70kva at 220v, so the secondary wire will be bigger of course. The reason for this is I have a buss plug that is 100 amps already from a different machine installed and was wondering if I could use it. The finished calculation would be 105 amps on 480v, and was hoping I could use it, if the powers that be would be okay with it.