With the amount of data required to do an accurate load calculation, the possibility of errors is increased. Even the computerized methods of load calculation are lacking in error checking procedures that could catch operator errors. For example, window areas can exceed wall areas, or wall areas facing north can be one square foot with a south wall of 300 square feet and east and west walls of 200 square feet. Many of the methods also oversimplified the process and gave insufficient options for climate, building assemblies (windows, doors, walls, etc.), and shading. Then there’s the effect of duct leakage that has only recently been investigated to any significant extent. As a result, cooling loads due to duct leakage are not included in any of the methods. Duct leakage has three effects on design cooling load. First, a supply leak is a direct loss in capacity. Second, a return leak will often bring in superheated attic air. Third, the difference between supply leakage and return leakage will cause increased infiltration. While it is tempting to treat duct leakage as additional infiltration, the effect is actually more complex and the answer is to always check out the duct work and repair the deficiencies. But attempting to get the proper size of air conditioning by the sq.ft. method is like throwing darts at the bulls eye by a novice player.