Dear Messrs cuky2000 , waross
Q1. "...The system could be designed with a [single feeder]* to the rail] and then [feeders]** running parallel to the rails to reduce the voltage drop]..."
A1. I may had miss-understood the configuration. I took at it that the [single feeder]* is protected by a Breaker A , feeding to a busbar B . Assuming three [feeders]** tapped the supply from the busbar B. Each [feeder]** shall be protected by an individual [feeder]** breaker X,Y,Z; which is sized to protect the feeder cable x,y,z. Load-break switches would NOT be acceptable, as they would NOT protect the feeder cable.
It shall be designed such that should the [single feeder]* breaker trips, it shall also trip out all the [feeder]** breakers. This is fine and good.
A2. However, consider what will happen when one or two of the [feeders]** breakers tripped. Unless any of the [feeders]** breakers trip is inter-locked to also trip off the feeder]* breaker, the single feeder cable which is remaining feeding the total (2 cranes) load would be heavily over-loaded/damaged! This is unacceptable.
A3. " Isolation problem" would arise. The only way to [isolate] the complete system is by switching off the feeder]* breaker or (all the three) [feeders]** breakers. The system will be "live ! " , if the feeder]* breaker and any one of the three [feeder]** breakers remain closed.
Che Kuan Yau (Singapore)