In recent years my employer installed several electrically driven gas compressors. Below 10,000 HP we chose induction motors driven by variable frequency drives and above that, synchronous motors driving variable speed transmissions, all driving centrifugal compressors.
We put in quite a few 15,000 and 22,000 HP synchronous motors in the 12.47-13.8 kV range. The motor breakers were 1200-amp VCB's with protection taken care of by microprocessor-based motor protection relays and the motor manufacturer's excitation controls. The electrical control and protection was pretty conventional, as one might imagine, but it was tied into compressor control and station control systems.
Previous problems with breakers failing to open caused us to use a breaker failure backup system. If a motor breaker was called upon to trip and failed to do so, we trip the bus incoming main. I find that prudent.
At another facility I work with, we have a couple dozen 4160-volt motors controlled by 5 kV circuit breakers. Again, motor protection relays provide the protection functions.
old field guy