At 100l/s you will already have a velocity of about 1,42m/s, which is fairly high. Others will have more practical insight her than me, but you have to be careful.
What is your situation?
Domestic, industrial or other? Pressure, length and type of outlet and branches. Limitations here, especially on pressure? Increase for normal use, or only firewater?
What are your pressure, and how much do you have to increase the pressure?
Some points:
By increasing the velocity, you also increases the possibillities of higher pressure peaks and water-hammer in the complete system.
There will be limits for valves and piping, highly depending on pressure class, type and not at least quality and actual present condition.
In my experience 4m/s would be a maximum for firewater conditions, 2 m/s for normal distributing mains, and in between you will find the normal flow speed for flushing of water main pipes!
I would not have increased the capacity at all, if there was an including clause that everything attached could withstand the increase.
If this is not the case I would put the sensible limit at 2m/s - giving a 40% increase to 140l/s.
Although other water systems uses much higher velocities, the great question here is the state of the existing pipeline and attached equipment, and the limits it actually was dimensioned for, and if on this base an increase is sensible at all.
I would like comments from others on this case!