Good morning,
I am sizing a fuse for a 1P 37.5kVA transformer that is tapped off of a 600V 3P 4w splitter. See below for one line:
________________________600V splitter 3p 4w
| |
| |
1P fuse 3P motors (200hp total)
|
|
1P 37.5kVA trafo
600V/240V
|
|
______240V 1P splitter
|
|
heater
I use ETAP for modeling and to model a 1P load a "phase adapter" is used, which I have set as a phase AB tap (therefore 600Vp-p).
Calculating the required primary fuse size (by Canadian Electrical Code) I have:
TX FLA: 37.5kVA / 0.6kV = 63A
fuse sized to 125% of FLA: 63 x 1.25 = 80A fuse
When I plot my TCC with the 240V single phase splitter as reference for the fuses I have selected, the 80A primary fuse (using a J class time delay) is far to the left of the transformer inrush of 12xFLA@0.1s. Strangely though, if I use the 600V splitter as reference the 80A primary fuse shifts to the right of the inrush (all other devices shift as they should to the new reference voltage). I am sure one of these TCCs is correct, but I need some guidance on whether I have sized this 1P primary fuse properly (see TCCs as well pariculary FU 1P HTR). Any ideas to what I am doing wrong?
Thanks in advance for the help
Tim
I am sizing a fuse for a 1P 37.5kVA transformer that is tapped off of a 600V 3P 4w splitter. See below for one line:
________________________600V splitter 3p 4w
| |
| |
1P fuse 3P motors (200hp total)
|
|
1P 37.5kVA trafo
600V/240V
|
|
______240V 1P splitter
|
|
heater
I use ETAP for modeling and to model a 1P load a "phase adapter" is used, which I have set as a phase AB tap (therefore 600Vp-p).
Calculating the required primary fuse size (by Canadian Electrical Code) I have:
TX FLA: 37.5kVA / 0.6kV = 63A
fuse sized to 125% of FLA: 63 x 1.25 = 80A fuse
When I plot my TCC with the 240V single phase splitter as reference for the fuses I have selected, the 80A primary fuse (using a J class time delay) is far to the left of the transformer inrush of 12xFLA@0.1s. Strangely though, if I use the 600V splitter as reference the 80A primary fuse shifts to the right of the inrush (all other devices shift as they should to the new reference voltage). I am sure one of these TCCs is correct, but I need some guidance on whether I have sized this 1P primary fuse properly (see TCCs as well pariculary FU 1P HTR). Any ideas to what I am doing wrong?
Thanks in advance for the help
Tim