We bought piece of equipment that has a 630VA control power transformer. When I add up the connected load I come up with over 800 VA connected to it. It feeds (2) small plcs and a little servo motor. I'm wanting to add a 30VA circuit to this. We are getting little help from the OEM on anything and they are in a foreign country. I'd ask them...but.
I notice this transformer has VDE rating of 800VA and another marking saying 2000VA. I don't know what this means. Attached is a picture.
It's protected by 2A fuses on the primary side.
My question is...would you change out this transformer to say a 1000VA or justify the extra loading by saying most likely the load is diversified. This is a brand new piece of equipment that has never been hooked up.
I notice this transformer has VDE rating of 800VA and another marking saying 2000VA. I don't know what this means. Attached is a picture.
It's protected by 2A fuses on the primary side.
My question is...would you change out this transformer to say a 1000VA or justify the extra loading by saying most likely the load is diversified. This is a brand new piece of equipment that has never been hooked up.