Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Size of earthing cable for a drive of 700 A

Status
Not open for further replies.

maypot

Electrical
Joined
Feb 25, 2005
Messages
108
Location
MU
Hi,

Basically what should be the size of the earthing cable for a drive 700A capacity driving a 400 k W motor @ 400 V 50 Hz.
I am using a 300 mm^2 copper cable on the power sides.
I trust that it should be at least the size of the power cable to sustain the current under fault condition.
Furthermore, the manufacturer of the VSD is requesting an earthing cable between the VSD and the motor.

Bob
 
You can calculate the min cross sectional area using:

S >= (SQRT(I^2t))/k

S = Cross sectional area of earth cable
I = Fault current
t = disconnection time
k = constant determined from tables related to initial temp of conductor & type of cable

(To BS 7671)
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top