dcset
Electrical
- Jul 12, 2009
- 40
Trying to start 4 motor 330kw and two motors of165 kw, on direct start Mechanical output 330 kw Volts 4160 V current nominal 68 A pf 0,72 eficiency 0,9 start current 243 A starting torque 0,94 pf on starting 0,1. the other motor dates are mechanical output 165 kw, volts 4160 V, currento full load 33 A, pf 0,72,eficiency 0,94, current on start 128 A, pf on star 0,16, i´m thinking on using a generator 4000 kva, pf 0,7, 4160 V eficiency 0,95, with a boost system to mantain excitation.
When i got all the motor except one started, i got nominal mechanical power from motors 1320 kw, electrical power kw demanded for the motors 1400,7 kw, and pf 0,72,
then we try to start one of the 330 kw motors on direct start, and i get 1663,350 mechanical power on starting, and 1663,35 kw electrical demanding on the start moment from the motor, this means diesel motor demands of 1750 kw mechanical on shaft, with a power demanded from generator of 3696 kva, and pf 0,45., i just wonder if generator is enough and if a motor of about 2177 kw mechanical will be enough.
Cause customers says me that as the motors are 6 poles and ten poles electrical motors, we have to uprate the unit, cause the generator is four poles, i couldn´t understand this point, for me doesn´t matter what is the internal poles of the motor, we are talking about power mechanical and electrical, i know i have two questions, first what do you think about my calculations, and second, what do you think about the question about relation between poles on generator and motor.
thanks a lot for your time
When i got all the motor except one started, i got nominal mechanical power from motors 1320 kw, electrical power kw demanded for the motors 1400,7 kw, and pf 0,72,
then we try to start one of the 330 kw motors on direct start, and i get 1663,350 mechanical power on starting, and 1663,35 kw electrical demanding on the start moment from the motor, this means diesel motor demands of 1750 kw mechanical on shaft, with a power demanded from generator of 3696 kva, and pf 0,45., i just wonder if generator is enough and if a motor of about 2177 kw mechanical will be enough.
Cause customers says me that as the motors are 6 poles and ten poles electrical motors, we have to uprate the unit, cause the generator is four poles, i couldn´t understand this point, for me doesn´t matter what is the internal poles of the motor, we are talking about power mechanical and electrical, i know i have two questions, first what do you think about my calculations, and second, what do you think about the question about relation between poles on generator and motor.
thanks a lot for your time