Hi, I am using RAM Connection Standalone. I am designing a Single Plate Connection (Beam to Column Flange) .
The beam is a W16x36 and the column a W10 x 33, both ASTM 992 G50. The Ultimate Shear is 39.01K = (1.2*19.44)+(1.6*9.80)
The plate is A36, 9" length, 1/4" thick, vert & horiz edge dist = 1.5" and the vertical center-to-center distance= 3". The weld size is 3/16"
I am using 3 bolts (1 column, 3 rows).
When I look at the Design Report, all design checks are OK except in the "PLATE (support side)" section,
here, I get :
Weld Capacity 64.71k Demand 39.01K OK
Reduction Factor 1
Calculation Eccentricity (in) = 2.5"
Bending at Weld Line Capacity = 7.54 k.ft Demand = 8.13 k.ft NO GOOD
I have successfully checked all the results manually except the Bending at Weld Line Capacity.
How do I calculate by hand the "Bending at weld line capacity" (7.54 k.ft) for a quick check ?
What is the procedure ?
I have tried several ways but I come up with different results, not the 7.54 k.ft
Thank you,
DanteQ
The beam is a W16x36 and the column a W10 x 33, both ASTM 992 G50. The Ultimate Shear is 39.01K = (1.2*19.44)+(1.6*9.80)
The plate is A36, 9" length, 1/4" thick, vert & horiz edge dist = 1.5" and the vertical center-to-center distance= 3". The weld size is 3/16"
I am using 3 bolts (1 column, 3 rows).
When I look at the Design Report, all design checks are OK except in the "PLATE (support side)" section,
here, I get :
Weld Capacity 64.71k Demand 39.01K OK
Reduction Factor 1
Calculation Eccentricity (in) = 2.5"
Bending at Weld Line Capacity = 7.54 k.ft Demand = 8.13 k.ft NO GOOD
I have successfully checked all the results manually except the Bending at Weld Line Capacity.
How do I calculate by hand the "Bending at weld line capacity" (7.54 k.ft) for a quick check ?
What is the procedure ?
I have tried several ways but I come up with different results, not the 7.54 k.ft
Thank you,
DanteQ