bbleiler
Electrical
- May 18, 2003
- 6
We manufacture aeration pumps/fountains. Our latest product line are large units, which use 7.5 & 10HP motors. Because of the weight of the units, about 200-250lbs., the capacitors for the single phase permanent split-capacitor (PSC) motor models are mounted on shore in the control cabinet. The aerators need to be GFCI protected. What we have found is that nuissance tripping of the GFCI occurs when the cable runs get too long. Things are generally fine up to 400' of 4/4 SOOW cable. We just finished testing a 600' length of cable. When the capacitors are in the control cabinet 600' away from the motor the GFCI trips immediately. When the capacitors are mounted inside the motor unit right at the motor connections everything is fine. One thing I have noticed is that when the capacitors are in the control cabinet the line currents show an imbalance, which seems to be proportional to length of the cable, meaning the longer the cable the greater the imbalance. When the caps are mounted in the motor unit the line currents are almost equal. Does anyone understand what is happening here? If it is the capacitive losses in the cable, why would the location of the capacitors matter?