Got a situation where I have joists breaking on a 2x4 stud wall. For many reasons, we cannot easily install a girder under the wall even though crawlspace piers exist at 10 ft. spacing.
The contractor has proposed fastening a single 1 3/4x16" LVL to the face of the stud wall tight to the bottom of the joists. He would support the LVL above each pier with a vertical 9 1/4" LVL that would have (4) studs behind it to brace it against weak axis bucking. The LVL columns would be blocked solid to the pier caps. The numbers work out on the LVL beams and columns as far as bending, deflection, bearing etc. My gut says another failure mode is the LVL beam and column just wanting to peel away from the stud wall. In reality, I doubt this is an issue.
FWIW, the load on each column is about 3.4 k.
Any thoughts or concerns?
If I have to, I can design everything as conventional 3 1/2" thick but the owner does not want to lose anymore square footage.
Thanks.
The contractor has proposed fastening a single 1 3/4x16" LVL to the face of the stud wall tight to the bottom of the joists. He would support the LVL above each pier with a vertical 9 1/4" LVL that would have (4) studs behind it to brace it against weak axis bucking. The LVL columns would be blocked solid to the pier caps. The numbers work out on the LVL beams and columns as far as bending, deflection, bearing etc. My gut says another failure mode is the LVL beam and column just wanting to peel away from the stud wall. In reality, I doubt this is an issue.
FWIW, the load on each column is about 3.4 k.
Any thoughts or concerns?
If I have to, I can design everything as conventional 3 1/2" thick but the owner does not want to lose anymore square footage.
Thanks.