ACI 318 allows the use of single layer wall reinforcing (single curtain) for walls less than or equal to 10" thick. anything thicker than 10" shall have (2) layers.
We did an inspection on a post-tension concrete slab on cast-in-place concrete shear walls structure. the concrete shear walls are the (2) stair cores at each end. they are 10" wall with single layer of reinforcing. we found diagonal cracks along the 2 faces of the shear wall cores from 1st to 5th floor consistently. these cracks were formed during construction on the 6th floor. no exterior envelope walls were constructed during that time, i.e. minimal wind.
In my opinion, these cracks are not due to wind given the heavy reinforcing in the walls and % of wind load the structure was seeing when the cracks formed. The structure is intended to be 16 stories tall, so at 6th floor construction with no envelope walls, the wall reinforcing, per our calculation, was way more than sufficient. Additionally, per our calculation, the overall design was in compliance to the code.
And that's what get us puzzled!
We suspect they are due to combined reasons:
1. the post-tension effect (precompression) of the slab, which caused forced displacement to the walls.
2. single layer of reinforcing which causes the wall to have 5" concrete until the stress hits the steel.
3. with early strength mix of PT slab, the wall strength may still be in 60% range, while the slab is being stressed.
Any input would be greatly appreciated. We are really puzzled by this phenomenon, and are wondering if any of you have seen this, that could share some insights.
Thanks.
Thanks.