Let me get an opinion on this... I've gotten different answers from different colleagues..
Single angle hanger, connected to the underside of concrete member with post-installed anchor bolts (yikes I know) - hanger steel bar welded to vertical leg of the angle applying tension to the vertical leg
What loads do the bolts need to designed for?
My initial thought was T(bolt) = T + (Tg)/e (tension due to load + added tension due to eccentrically applied load, resolved into a tension/compression)
after talking with other engineers and researching some.. AISC prying action could apply?
So in summary, my questions:
1. What are the resulting loads in the bolts?
2. When using the AISC Prying Action equation, if t > treq, does the tension in the bolts = T/n (no added tension from any eccentricity to be considered)?
3. PCI also has a method in chapter 6, which is slightly different than the 2 above, would this be acceptable for the described condition?
4. Should the angle be checked for bi-axial bending - strong axis bending (angle spanning between the bolts) + torsion (due to load applied at the vertical leg, thus eccentric to the centroid)
TIA for the help.
Single angle hanger, connected to the underside of concrete member with post-installed anchor bolts (yikes I know) - hanger steel bar welded to vertical leg of the angle applying tension to the vertical leg
What loads do the bolts need to designed for?
My initial thought was T(bolt) = T + (Tg)/e (tension due to load + added tension due to eccentrically applied load, resolved into a tension/compression)
after talking with other engineers and researching some.. AISC prying action could apply?
So in summary, my questions:
1. What are the resulting loads in the bolts?
2. When using the AISC Prying Action equation, if t > treq, does the tension in the bolts = T/n (no added tension from any eccentricity to be considered)?
3. PCI also has a method in chapter 6, which is slightly different than the 2 above, would this be acceptable for the described condition?
4. Should the angle be checked for bi-axial bending - strong axis bending (angle spanning between the bolts) + torsion (due to load applied at the vertical leg, thus eccentric to the centroid)
TIA for the help.