Simultaneous Shear And Tension on threaded rod 1
structurebeton
When there is simultaneous Tension (fa) and Shear(fv) on a threaded rod (or a bolt) would you verify separately each case against the allowable fv/Fv <1 and fa/Fa<1 , or would you add those to do one verification fv/Fv+fa/Fa < 1 ?
You need to account for shear/tension interaction. For bolts, see AISC spec section J. For threaded rods, the unity equation you gave is conservative.
Assuming the stresses are below yield, the interaction formula is:
(&[ignore]sigma[/ignore];/&[ignore]sigma[/ignore];y) + (&[ignore]tau[/ignore];/&[ignore]tau[/ignore];y) &[ignore]le[/ignore]; 1
where
&[ignore]sigma[/ignore]; = applied tensile stress
&[ignore]sigma[/ignore];y = tensile yield stress
&[ignore]tau[/ignore]; = applied shear stress
&[ignore]tau[/ignore];y = shear yield stress
I erred in my previous post - each ratio should be squared:
(&[ignore]sigma[/ignore];/&[ignore]sigma[/ignore];y)2 + (&[ignore]tau[/ignore];/&[ignore]tau[/ignore];y)2 &[ignore]le[/ignore]; 1
where
Thanks CoryPad,
Can you give a reference on that formula?
Handbook of Bolts and Bolted Joints, edited by Bickford and Nassar, page 408. More generically, it can be derived using the von Mises/distortion energy yield criterion.