HamburgerHelper and jghrist , thank you for you time and interest.I know It s too simple.
Please check values than you will understand my point.
I will attach here my protection relay set screen .
And the values which I injected as secondary are like below;
Gen Side : HV (Y Side)
I1: 0,083 0° I1: 0,083 -150°
I2: 0,083 -120° I2: 0,083 -270°
I3: 0,083 -240° I3: 0,083 -30°
At the values, Relay dont trip. There is balanced and no differential .
According to jghrist and all informations which i know, It should be -30° ,not -150°.