Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Sidewall Sprinkler Head with Pendant Sprinkler in Coverage Area

Status
Not open for further replies.

fpumd

Mechanical
Joined
Oct 2, 2017
Messages
1
Location
US
Hi all,

I am trying to install a sidewall sprinkler head with a coverage area of 14' x 14'. The room has a pendant sprinkler that is less than 6' away from where the sidewall sprinkler would be located. NFPA 13 code 8.7.3.1.6 states that there cannot be adjacent or opposite sidewall heads in the same room and 8.7.3.4 states that sidewall heads cannot be less than 6 feet apart. If the other head in the room (pendant head) is within 6 feet and adjacent to the sidewall head, is this allowed? The pendant head would be approximately 3" below the ceiling and the sidewall is 6 inches below.

Reference NFPA 13 Codes:
8.7.2.2.1
8.7.2.2.2
8.7.3.4
8.7.3.1.6
 
 http://files.engineering.com/getfile.aspx?folder=54bca95d-dcee-4e88-9563-f3459f65cfbb&file=Sidewall_Sprinkler_Question.dwg
Well some reason I cannot open the link.

Is the pendant directly in front of the sidewall??

I would say yes you have to follow the minimum six foot rule.

Unless one is shielded in someway
 
First, it is customary to send a pdf or picture of the file, not an autocad drawing.

For your first problem, yes, if the spray can reach the pendent, then you must comply with the 6'-0 rule.
Second one, stagger the sidewalls. This way you can meet the 14' between.

R/
Matt
 
Without seeing a drawing
I guess the other question is why do you need the two sprinklers on the same area??
It seems like one, maybe the sidewall would cover everything
 
Doesn't look like a legal arrangement. Also it appears your pendent is 3" off the wall which the minimum is 4".

8.7.3.4 addresses sidewall sprinklers on the same wall so it doesn't apply here.

8.7.3.1.6 is correct that the pendent cannot be in the discharge of the sidewall unless the pendent is somehow obstructed from the spray of the hsw.

If your pendent is to protect under an obstruction you may consider moving your hsw to throw under it.

EDIT: you can put sidewall sprinklers on opposite or adjacent walls of a room, they simply need to be outside the maximum area of the adjacent sprinklers.
 
I didn't go to the pic, but if the pendent head is within three inches of the wall , can't it just be changed to a vertical sidewall head and call it good?

Alex Traw
Rainbow Fire Sprinklers
Albany, Oregon
 
Deflectors shall be 4"-6" from the wall from which they are projecting 8.7.4.1.2.1*

Horizontal sidewall deflectors may be less than 4" but not vertical sidewalls. 8.7.4.1.2.2
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top