In the oil and gas industry, the maximum shutoff pressure is taken as the maximum ANSI class pressure. So, on a 300# system, the shutoff pressure (actually, it is a differential since we also assume atmospheric on the other side) is 740 psi.
This is process shutoff pressure. It has nothing to do with sizing the actuator.
For the actuator, we size the actuator on 80 psig minimum (if you use less, say 70 psig, then you will need a larger actuator). On most I/A system, you will have around 100 psig for your valve.
Add to it the valve friction and then add 40% safety margin, you now have the torque requiremnt to actuate the valve.
This is also the spring's (on the spring return) torque requirement.
Should there then be a closing time requirement, then you may need to go even larger.