Can anyone tell me how fast a shunt trip device opens a 480V breaker, typically anyway? I assume it varies with design. Do any designs reliably trip in < 5 cycles? Can anyone send a link to a shunt trip spec sheet showing trip times?
I have a collection of 480V MCCs fed by 480V power switchgear. The power switchgear feeders have ground fault trips. I am trying to determine if a ground fault sensor + a shunt trip scheme in the MCC buckets can operate fast enough to trip ahead of the ground fault trips in the power switchgear. The pwr swgr feeder grounds trip in the 0.15-0.25sec range, but could be slowed down if we wanted to accept loosing coordination with the bus ties.
I have a collection of 480V MCCs fed by 480V power switchgear. The power switchgear feeders have ground fault trips. I am trying to determine if a ground fault sensor + a shunt trip scheme in the MCC buckets can operate fast enough to trip ahead of the ground fault trips in the power switchgear. The pwr swgr feeder grounds trip in the 0.15-0.25sec range, but could be slowed down if we wanted to accept loosing coordination with the bus ties.