Shunt Reactor Bank calculations
anteg
I am trying to calculate the size of inductors for a three phase shunt reactor bank to provide 3MVAR at 33kV.
Calculations
XL=(kV^2)/MVAR = 33^2/3 = 363 ohms
L= XL/(2piF)= 363/376.99 = 0.962 Henries
Is this value correct, if so will the bank require an indcutor of 0.962 henries per phase?
This is where I get a little confused. Will three 0.962 Henry reactors (one per phase) form a 0.962 reactor bank?
I know that with capacitor banks a 600 kVar bank is formed of 3- 200kVar units. 200 kVar per phase.
I just realized my last question does not make much sense..
what I meant to ask was if three inductors of 0.9 henries (one per phase) will give me a 3MVAR bank at 33kV? based on shown calculations.
anteg,
What you've done is correct. You can use either
3-phase MVA and kV ph-ph
or
1-phase MVA and kV ph-n
Both will give you the same result.
Why do you think you need reactors? I have installed caps on a 34.5 kv line and used fused cutouts.
I think it's good for you to understand the calculations.
However, you can simply tell your reactor supplier the voltage and MVAr you need and they'll take it from there.
Scottf,
It is true that I can just let someone else handle this, but I would like to understand what needs to be done before we move forward with a project.