I am evaluating whether additional reinforcing steel is required in a shotcrete retaining wall (with soil nails) to reduce shrinkage cracks. Overexcavation was required to construct the wall. The average overexcavation depth (thickness) is about 4 inches, and is up to about 16 inches at some locations. The wall design calls for an 8-inch-thick wall reinforced with two layers of 4 x 4 W4 x W4 mesh and continuous horizontal bars behind the bearing plates at each soil nail row. Soil nails are spaced every 5 vertical feet.
Because of the overexcavation, the as-built wall thickness is 12 inches average, and up to 24 inches at some areas.
The plans call for additional continuous horizontal rebars to reduce shrinkage cracks depending on the as-built wall thickness (because of overexcavation) as follows:
wall thickness = 10" - #3 @ 16" o.c.
12" - #3 @ 12" o.c.
14" - #3 @ 14" o.c.
16" - #3 @ 8" o.c.
I think the additional steel for shrinkage crack reduction is based on ACI guidelines for minimum steel area as a percentage of reinforced concrete area for a slab (but not sure).
Shotcrete and mesh is placed as followes:
1) backfill shotcrete in overexcavations and out to first mesh layer
2) hang first mesh layer
3) shotcrete to second mesh layer
4) hang second mesh layer
5) shotcrete to wall face and rod finish
I am uncertain of the effect that phasing of shotcrete placement has on shrinkage cracking, and whether the additional steel is necessary (and where it should be placed).
Please provide input on whether additional steel is required as scheduled (and whether the phasing of shotcrete precludes the need for it), and if so, whether the amount called for is reasonable (or not enough). Also, where should the additional steel be placed?
The AASHTO manual for soil nail wall design does not address design of additional steel to reduce shrinkage cracks.
Because of the overexcavation, the as-built wall thickness is 12 inches average, and up to 24 inches at some areas.
The plans call for additional continuous horizontal rebars to reduce shrinkage cracks depending on the as-built wall thickness (because of overexcavation) as follows:
wall thickness = 10" - #3 @ 16" o.c.
12" - #3 @ 12" o.c.
14" - #3 @ 14" o.c.
16" - #3 @ 8" o.c.
I think the additional steel for shrinkage crack reduction is based on ACI guidelines for minimum steel area as a percentage of reinforced concrete area for a slab (but not sure).
Shotcrete and mesh is placed as followes:
1) backfill shotcrete in overexcavations and out to first mesh layer
2) hang first mesh layer
3) shotcrete to second mesh layer
4) hang second mesh layer
5) shotcrete to wall face and rod finish
I am uncertain of the effect that phasing of shotcrete placement has on shrinkage cracking, and whether the additional steel is necessary (and where it should be placed).
Please provide input on whether additional steel is required as scheduled (and whether the phasing of shotcrete precludes the need for it), and if so, whether the amount called for is reasonable (or not enough). Also, where should the additional steel be placed?
The AASHTO manual for soil nail wall design does not address design of additional steel to reduce shrinkage cracks.