Should I use MWFRS or C&C wind load for designing foundations of a building

Status
Not open for further replies.

structguy777

Structural
Jun 30, 2015
2
I am designing shallow foundations only for a building - which has no columns - it has channels at the bottom and cladding all around. The channels at the bottom will sit directly on the shallow foundations. Should I use MWFRS or C&C wind load to get the reactions at the bottom? I think I should use C&C wind load. Please confirm.
 
Replies continue below

Recommended for you

What is your tributary area affecting the footings? Typically if it is more than 700 s.f. I use MWFRS.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
MWFRS for the foundation. C&C if it was a single component with little redundancy.

When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.

-R. Buckminster Fuller
 
@JAE - There are 14 shallow foundations supporting the entire building. Largest tributary are for a footing is 213 SF. Can you please tell me from where did you get 700 SF as criteria for using MWFRS?

@manstrom - There are 14 shallow foundations supporting the entire building. Why should I use MWFRS?

Should I use C&C for the roof?
 
If they are a part of the Main Wind Force Resisting System, and are resisting the overturning / sliding of the entire building globally, then I would use MWF.

Use whatever you want.

When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.

-R. Buckminster Fuller
 
ASCE 7-10 30.2.3 Tributary Areas Greater than 700 ft2 (65 m2) -- Component and cladding elements with tributary
areas greater than 700 ft2 (65 m2) shall be permitted to be designed using the provisions for MWFRS.
 
structguy777 (Structural), can you rovide a pic or sketch of building so I can tell you what to use

A 3D sketch or pic or freehand sketch will help visualize your case
 
Thanks, Jerehmy for looking that up.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
A lot of engineers argue foundations are always MWFRS regardless of tributary area.
 
I agree with abusementpark. The foundations are neither cladding or a component that delivers wind load to the lateral force resisting system, so they should be designed for MWFRS.
 