Our shop has 240 3 ph 60 Hz, and we need to run a short term (several 5 minute tests) on some equipment needing 480 3 ph.

We have a disconnected distribution transformer, 480 Y / 240 delta 150 A secondary, which is at least 30 times the ampacity needed for the test.

Is it OK to backfeed 240 into this to obtain the 480??

Thanks in advance!
 
Yes, but there are various code rules that would have to be complied with.
 
Your initial current inrush may be over 1000 Amps. You may need dual element fuses to get this energized.


Bill
--------------------