I’m developing an LV switchboard replacement programme and am in the spec review stage prior to going out to tender. I’ve identified what I believe is a problem with the fault rating of the original switchgear and would appreciate some thoughts.
The boards are designed as a three-section type with one incomer per section and a bus section switch between the A and B sections, and another between the B and C sections. There is no interlocking between the incomers and bus section switches giving rise to a condition where we have the potential for two or conceivably three sources feeding one bar with one or both bus section switch(es) closed, a situation which will take the fault level massively over the ACB rated breaking capacity and also exceed the rated capacity of the bus bracing. The normal operating condition is for the bus section switches to be open and in this situation the board is adequately rated.
Paralleling is necessary in order to avoid interrupting the process and is controlled procedurally. The switching process is a manual local operation. Paralleling only occurs for a short period when one source has to be taken out of service or is being returned to service. My opinion is that the bar and breakers must be rated for the maximum foreseeable fault. I think the condition where three sources are in service and both bus section switches are closed could be prevented by a 4-out-of-5 key exchange interlock, leaving the worst case as two sources with a closed bus section switch between them and the third bus section on a single source.
‘Others’ here believe that exceeding the rated fault level for the short term parallel operation is an acceptable risk because ‘that is how it has always been done’. I disagree and think there is no acceptable excuse for exceeding the equipment rating, particularly when modern gear is capable of meeting the requirement even if the old gear we are replacing, which is roughly 40 years old, couldn’t do so. I’m especially unhappy because it’s likely that I will be expected to sign off this design, and I’m going to raise a few eyebrows if I refuse to do so. I had hoped not to rock the boat too much in my new job until I’d had time to settle in but it seems I’m back to my old tricks.![[smile] [smile] [smile]](/data/assets/smilies/smile.gif)
----------------------------------
If we learn from our mistakes I'm getting a great education!
The boards are designed as a three-section type with one incomer per section and a bus section switch between the A and B sections, and another between the B and C sections. There is no interlocking between the incomers and bus section switches giving rise to a condition where we have the potential for two or conceivably three sources feeding one bar with one or both bus section switch(es) closed, a situation which will take the fault level massively over the ACB rated breaking capacity and also exceed the rated capacity of the bus bracing. The normal operating condition is for the bus section switches to be open and in this situation the board is adequately rated.
Paralleling is necessary in order to avoid interrupting the process and is controlled procedurally. The switching process is a manual local operation. Paralleling only occurs for a short period when one source has to be taken out of service or is being returned to service. My opinion is that the bar and breakers must be rated for the maximum foreseeable fault. I think the condition where three sources are in service and both bus section switches are closed could be prevented by a 4-out-of-5 key exchange interlock, leaving the worst case as two sources with a closed bus section switch between them and the third bus section on a single source.
‘Others’ here believe that exceeding the rated fault level for the short term parallel operation is an acceptable risk because ‘that is how it has always been done’. I disagree and think there is no acceptable excuse for exceeding the equipment rating, particularly when modern gear is capable of meeting the requirement even if the old gear we are replacing, which is roughly 40 years old, couldn’t do so. I’m especially unhappy because it’s likely that I will be expected to sign off this design, and I’m going to raise a few eyebrows if I refuse to do so. I had hoped not to rock the boat too much in my new job until I’d had time to settle in but it seems I’m back to my old tricks.