If you are referencing ANSI standard, the damage curve for transformer rated at 30MVA is given as 2 seconds. For smaller transformer the withstand time is at 1 second for capacity rating not exceeding 0.5MVA. As in the case of IEC 76, the compliance short circuit duration is also 2 seconds. However, for longer duration short circuit withstand time, the requirement should be specified to the manufacturer.
For your information ANSI has provided short circuit withstand time against the symmetrical short circuit current. Based on the impedance, the higher the impedance value the higher it will be the withstand time as the fault current is reduced by the impedance. However the time is limited to 5 seconds.