I assume that "the short circuit power" at the MV side of a 11kV/415V transformer is 250 MVA.
If the TX is rated at 1500 kVA, then the short circuit at the LV terminals is "calculated" to be 34 kA, approximatively.
Put 3 TX in parallel, and the short circuit should become: 3x34= 102 kA.
The question is: someone is saying that even though the above calculations are correct, they do not correspond to reality. In reality, the sc would be "around 65 kA" only.
Which one is correct? The panelboard can cost double in one alternatvie than the other.
I assume that "the short circuit power" at the MV side of a 11kV/415V transformer is 250 MVA.
If the TX is rated at 1500 kVA, then the short circuit at the LV terminals is "calculated" to be 34 kA, approximatively.
Put 3 TX in parallel, and the short circuit should become: 3x34= 102 kA.
The question is: someone is saying that even though the above calculations are correct, they do not correspond to reality. In reality, the sc would be "around 65 kA" only.
Which one is correct? The panelboard can cost double in one alternatvie than the other.