Dear Mr. KRC83 (Electrical)
"...When Low Voltage MCCB say 200A 22kA 240AC is tested for short circuit test can anyone provide below information
1. How to calculate internal pressure generated in an enclosure
2. how to calculate energy released during test and how to co-relate it with pressure generated..."
Che. 1. Following are the main standards : In the IEC world IEC 60947-1,2 ; in the US world ANSI C37.50. The test requirements differs.
2. IEC 60947-2 sub-clause 8.3.2.1 states.......
a) Circuit breaker shall be tested in free air,
b) ... if a CB may be used in specified individual enclosure and has been tested in free air, it shall be additionally tested in the smallest of such enclosure... where the details including the dimension of the enclosure, shall be stated in the test report...
3. Arrangement of the short-circuit opening/closing test, the bolted shorting is NOT on the [CB load terminals] but some distance away. There is NO arc at all at the bolted shorting point. On the other hand, heavy arc across the CB during closing/opening on a short-circuit test. On various short-circuit tests conducted in England, Australia and Sweden that I witnessed, the lab does NOT record the [over-pressure] on an open air test.
4. However, the [over pressure] is of great importance under a different standard e.g. IEC 61439-1,2 etc., where the criterial are listed.
Che Kuan Yau (Singapore)