Mr. Bill,
I should have been more specific about when the maximum force occurs---and thank you for noting I was not clear on that specific point. Actually there were several points which needed additional explation.
Concerning when the maximum force occurs.
The maximum force occurs when the short circuit occurs 45 degrees after the zero current in Phase B. The maximum force will then occurs 1/2 cycle after the instant of the short circuit. Any other combination of circumstances will produce a smaller value.
Stanley Killian, he was a Developmet and Research Engineer for Delta Star Electric Company (Chicago), describes this in greater detail in "Forces Due to Short Circuit Currents" Electrical World, December 12, 1942.
Also concerning the Bracing Requirements
Often, or sometimes, the bus bars are not in the same plane. That is they are in a staggered plane or they contain bends. Not an easy solution to this. Here is what is happening. When the forces are not in the same plane, the forces causes the buses to want to "twist" or rotate so the bus bars will need to resist this motion. I solve this by calculating the bracing distance for buses in the same plane and adding a brace in the middle of the calculation. For example, Rather than 12 " I would add one at 6 inches.
Another item concerning bracing.
To really calculate the bracing distances, you need to know the exact yield strength (PSI) of the bus bar material. Most calculation are for copper. Aluminum alloy are now almost equal to the yield of Copper. The calculations are made for copper and then adjusted for AL. For example if the yield strength of aluminum is 6000 PSI and copper is 15,000 PSI, then the calculations are adjusted to {6000/15000}^0.5 =0.633 of the distance for copper material. So you calculate 10 inch bracing for copper and for Al the bracing requirement is 10*.633 = 6.33 inches. It all depends on the yield strength for the material used in your calculations.
I Hope this helps and many thanks to Bill for asking that question. I was in a hurry and should have taken the time to fully explain. Sorry!
Also, there appears to be significant interest in this subject as the insurance companies for industrials ask for short circuit and flash hazard calculations. I have helped several solve these problems and avoid a replacement or rebuild.
The basic engineering for this topic can be found in the work by C.H. Van Aspen of Hydro Electro Power Comission of Ontario -1922 and also H.B Dwight.
Jack