Hi davidbeach
Thanks for the reply. I think we are in agreement.
As to voltage adjustment, In my experience this is usually done on the basis of open circuit voltage to compensate for cronically high or low primary voltages. If there is a further problem, usually with fluctuating primary voltages, the taps may be adjusted to a different value. This is invariably a compromise.
In regards to added impedance, a 2% transformer and a 3% transformer will usually be set on the same taps and deliver the same open circuit voltage. If a 2% transformer is used and the impedance seen from the main breaker is increased to 3% either by the feeder impedance, an added reactor or a combination of the two, the effect will be the same as if a 3% transformer was used and there was no feeder impedance.
Respectfully