Your generator will contribute positive and negative sequence fault current, as the zero sequence is blocked. This contribution will be limited by the transformer impedance, as jbartos suggests and it's unlikely to be the utility's main concern. They will be more interested in assuring that energization of their de-energized line is prevented during maintenance, for personnel safety. In any event, these are matters that should be addressed jointly with the electric utility.